Hi,
I am using UAExpert client for verifying my newly created nodemanager for OPC CPP Server.
When I try to connect to the server, I get read request for Node Id : 2255, 84 , 2259, 2253 and so on.
My node manager implementation is not complete and I have many more nodes to be initialized and added to the address space.
Hence I would like to know how many mandatory nodes needs to be in the address space for verifying my
CPP Server with the UAExpert.
Thanks & Regards,
Indu
Read Request from UAExpert
Moderator: uaexpert
-
- Hero Member
- Posts: 23
- Joined: 02 Sep 2011, 06:15
Read Request from UAExpert
Last edited by induna23 on 07 Feb 2013, 10:48, edited 1 time in total.
- Support Team
- Hero Member
- Posts: 3064
- Joined: 18 Mar 2011, 15:09
Re:Read Request from UAExpert
The NodeIds that are mandatory according to UA are defined in the OPC UA Specification Part 5 (Information Model), beginning in chapter 8.
The NodeIds the UaExpert needs as a minimum requirement are:
- Root and the Objects folder (it will browse them on connect)
- NamespaceArray (child of the Server node)
- State (child of Server/ServerStatus)
Please notice that these are the minimum requirements for the UaExpert to display reasonable information, but for full functionality the complete UA address space (especially the Types tree) is required to be implemented.
The NodeIds the UaExpert needs as a minimum requirement are:
- Root and the Objects folder (it will browse them on connect)
- NamespaceArray (child of the Server node)
- State (child of Server/ServerStatus)
Please notice that these are the minimum requirements for the UaExpert to display reasonable information, but for full functionality the complete UA address space (especially the Types tree) is required to be implemented.
Last edited by Support Team on 07 Feb 2013, 10:48, edited 1 time in total.
Best regards
Unified Automation Support Team
Unified Automation Support Team
- Support Team
- Hero Member
- Posts: 3064
- Joined: 18 Mar 2011, 15:09
Re:Read Request from UAExpert
This topic is solved and has been locked by the administrator.
For new issues, please create a new topic.
For new issues, please create a new topic.
Best regards
Unified Automation Support Team