UaGateway does not change the value of items when are subscribed by Sampling

Post by jfr1982 »

Hi,

I have purchased UaGateway to connect an OPC DA Server and serve the items through the OPC UA Server.
We have an OPC UA Client connected that has some items configured with Sampling as MonitoringMode, with this mode configured the OPC UA Server is not changing the values.
Is there any configuration parameter to allow the clients to use Sampling as Monitoring Mode?

Regards

User avatar
Support Team
Hero Member
Hero Member
Posts: 3064
Joined: 18 Mar 2011, 15:09

Re: UaGateway does not change the value of items when are subscribed by Sampling

Post by Support Team »

Hi,

the MonitoringMode "Sampling" does not allow any notifications being reported, hence behavior of UaGateway is exactly as expected. Please carefully read the OPC UA Specification-Part 4 (Table 7.18):

MonitoringMode:
DISABLED=The item being monitored is not sampled or evaluated, and Notifications are not generated or queued. Notification reporting is disabled.
SAMPLING=The item being monitored is sampled and evaluated, and Notifications are generated and queued. Notification reporting is disabled.
REPORTING=The item being monitored is sampled and evaluated, and Notifications are generated and queued. Notification reporting is enabled.

To make a long story short, you must use "Reporting" to see something moving with your data.
Best regards
Unified Automation Support Team