Hi,
I'm using the evaluation version of the product and I'm able to connect to an AE Server (Siemens Open PCS7) using OPC-UA Alarms. But they have some custom way of requesting historical alarms... To do this, the OPC AE Client must be able to :
- support the "SetFilter" functionality for a subscription,
- set this kind of filter : "OPCHAEServer hmode=advise htStartTime=NOW-30M"
- then call refresh of the subscription
Does the product support this? And if yes, how to I set this kind of filter with my OPC-UA Client? I know about the Select and Where clause of the filter in OPC-UA but I've no idea how to map this to A&E Filter.
Thanks.
Best regards
OPC AE Filter and using it from OPC-UA
Moderator: uagateway
- Support Team
- Hero Member
- Posts: 3069
- Joined: 18 Mar 2011, 15:09
Re: OPC AE Filter and using it from OPC-UA
Hello,
the "filter" is not mapped through the UaGateway, because there is no "generic" way to do such mapping.
If the OpenPCS7 is not able to operate without setting any filters, you can not use the UaGateway.
The UaGateway can not implement some vendor specific funcitonalities, therefore the UaGateway just pass through (un-filtered) Alarms. The reveicer must filter/disgard by himself.
the "filter" is not mapped through the UaGateway, because there is no "generic" way to do such mapping.
If the OpenPCS7 is not able to operate without setting any filters, you can not use the UaGateway.
The UaGateway can not implement some vendor specific funcitonalities, therefore the UaGateway just pass through (un-filtered) Alarms. The reveicer must filter/disgard by himself.
Best regards
Unified Automation Support Team