Hello, i was using the UaSdkCClient 1.9.1 version on linux without any problem but now when i tried to upgrade to the 1.9.2 version, i can't even connect me to the PLC. The errror i get is :
*****************************************************
405|W|96358280* ProcessOpenSecureChannelResponse: revised lifetime 3600000 below limit 4294967040.
.405|W|96358280* ProcessOpenSecureChannelResponse: Handling error 0x80AB0000.
:OPC_ConnectError_CB:
: ServiceType: OpenSecureChannel
: Error: 0x80ab0000
: Overridable: false
*****************************************************
even after several reconnection attempts the same errors appears.
To fix it, i tried these 3 methods :
1) I change the SecureChannelLifetime (by example to 4294967041) in the client_settings.conf file but the errors appears again : "revised lifetime 3600000 below limit 4294967040."
2) I manually change the SecureChannelLifetime of the UaClient_Session but the errors appears again : "revised lifetime 3600000 below limit 4294967040."
3) I manually change the SecureChannelLifetime of theUaClient_Configuration but the errors appears again : "revised lifetime 3600000 below limit 4294967040."
I realized that no matter where I try to change the SecureChannelLifetime (to make it superior than the limit 4294967040 mentioned in the error message), my change does not take effect and it is always the value 3600000 that remains. Can you tell me where to really modify it or how to solve my problem please.
Thanks
Problem of migration to the new ANSI C based OPC UA Client SDK v1.9.2
Moderator: uasdkc
-
- Full Member
- Posts: 5
- Joined: 08 Apr 2021, 08:55
- Support Team
- Hero Member
- Posts: 3074
- Joined: 18 Mar 2011, 15:09
Re: Problem of migration to the new ANSI C based OPC UA Client SDK v1.9.2
Hi,
The value you are requesting "4294967040" is to big, my educated guess is that on client side both min. and max. secure channel lifetime seems to be "-1" (the initialization value), it was probably not set at all. You have to request a value smaller or equal to one hour and of course your own Min and Max settings should reflect that range as well, or at least have overlap with the server side, otherways negothiation will fail.
the server obiously has a maximum secure channel lifetime of 3600000 (one hour). However your Client demands a much higher value (longer) lifetime, hence being rejected with error. Therefore if you change the requested lifetime in the client_settings it should be in the range accepted by the server (which is most likely something between 10 min and 1 hour).revised lifetime 3600000 below limit 4294967040
The value you are requesting "4294967040" is to big, my educated guess is that on client side both min. and max. secure channel lifetime seems to be "-1" (the initialization value), it was probably not set at all. You have to request a value smaller or equal to one hour and of course your own Min and Max settings should reflect that range as well, or at least have overlap with the server side, otherways negothiation will fail.
Best regards
Unified Automation Support Team
Unified Automation Support Team
-
- Full Member
- Posts: 5
- Joined: 08 Apr 2021, 08:55
Re: Problem of migration to the new ANSI C based OPC UA Client SDK v1.9.2
Hello,
I confirm that the min and max of the secure channel lifetime are set to 300000 and 3600000 in the settings file. So, even with the max at 3600000, i still have the same error
I confirm that the min and max of the secure channel lifetime are set to 300000 and 3600000 in the settings file. So, even with the max at 3600000, i still have the same error
-
- Full Member
- Posts: 5
- Joined: 08 Apr 2021, 08:55
Re: Problem of migration to the new ANSI C based OPC UA Client SDK v1.9.2
Hello,
Is there a problem with the new ANSI C based OPC UA Client SDK v1.9.2 ? Because even with good configurations :
SecureConnection_MinRevisedSecureChannelLifetime set to 300000
SecureConnection_MaxRevisedSecureChannelLifetime set to 3600000
and the SecureChannelLifetime set to 3600000,
my error is still the same :
*****************************************************
405|W|96358280* ProcessOpenSecureChannelResponse: revised lifetime 3600000 below limit 4294967040.
.405|W|96358280* ProcessOpenSecureChannelResponse: Handling error 0x80AB0000.
:OPC_ConnectError_CB:
: ServiceType: OpenSecureChannel
: Error: 0x80ab0000
: Overridable: false
*****************************************************
I still don't have any solutions
Is there a problem with the new ANSI C based OPC UA Client SDK v1.9.2 ? Because even with good configurations :
SecureConnection_MinRevisedSecureChannelLifetime set to 300000
SecureConnection_MaxRevisedSecureChannelLifetime set to 3600000
and the SecureChannelLifetime set to 3600000,
my error is still the same :
*****************************************************
405|W|96358280* ProcessOpenSecureChannelResponse: revised lifetime 3600000 below limit 4294967040.
.405|W|96358280* ProcessOpenSecureChannelResponse: Handling error 0x80AB0000.
:OPC_ConnectError_CB:
: ServiceType: OpenSecureChannel
: Error: 0x80ab0000
: Overridable: false
*****************************************************
I still don't have any solutions
- Support Team
- Hero Member
- Posts: 3074
- Joined: 18 Mar 2011, 15:09
Re: Problem of migration to the new ANSI C based OPC UA Client SDK v1.9.2
Hi,
we have checked the client-side SDK code and the provided client-side examples again, the Min and Max settings for the SecureChannelLifetime all work as expected. We can not see any migration issue from 1.9.1 to 1.9.2 here. We have "migrated" the examples ourselves, without changing a single line of code.
The only explanation we have is: you have initialized the stack early without proper loading the settings before, or you may accidently have overwritten the revised limit at a later stage in your code.
we have checked the client-side SDK code and the provided client-side examples again, the Min and Max settings for the SecureChannelLifetime all work as expected. We can not see any migration issue from 1.9.1 to 1.9.2 here. We have "migrated" the examples ourselves, without changing a single line of code.
The only explanation we have is: you have initialized the stack early without proper loading the settings before, or you may accidently have overwritten the revised limit at a later stage in your code.
Best regards
Unified Automation Support Team
Unified Automation Support Team