Hello,
I have two PLCs I want to connect to FLEXSIM through OPC using UAGateway as a proxy (OPC UA to OPC classic).
Endpoints are as following:
PLC 1 : opc.tcp ://192.168.0.11:4840
PLC 2 : opc.tcp ://192.168.0.5:4840

I got Error while trying to connect two S7 1500 OPC UA Servers to UA Gateway at the same time:
- The first server connects correctly
-The second server could not connect , error message: "Configuration error - Duplicated Server"

Do you have any idea how to solve this problem

Thank you for your help

Best Regards
hbbend
Jr. Member
Jr. Member
 
Posts: 1
Joined: 09 May 2017, 13:26

Re: Error connecting two S7 1500 OPC UA Servers at the same

Postby Support Team » 27 Feb 2019, 18:19

Hello hbbend,

you can configure UaGateway only to connect to the same server once. To identify a server we use the entry on index 1 in the namespace array (which is equal to the ApplicationUri).
So I assume both instances of S7 1500 UaServers are configured to use the same ApplicationUri. You need to change that in the configuration tool shipped with the UaServer.
Best regards